Hey all,

Since my summer rebuild project has stalled, I've decided to tackle another problem. I need to do some welding on my subframe, and my garage is severely underpowered for that. I only have one 15A breaker to the garage which ain't gonna cut it.

So I'm running a 100A trunk from the main panel in the basement up and out to the garage, which is about a 25' run. I've got the panel and necessary breakers - 1 50A (welder), 2 15A, 1 20A. I'm putting a dual pole 100A breaker from the main panel to bring 110/220 to the garage.

My question is - what wire to run from the main panel to subpanel in the garage? I've searched online and found either #4 or #3 cu wire. Also looks like 1 1/2" conduit is required, which seems kinda big, but so is the wire. Any suggestions would be appreciated.

For now I'm just gonna hook up the 50A plug for the welder. My neighbor has a Miller 210 I can borrow to weld a couple of things and get going.

Thanks!


Top
 Profile E-mail  
 
 Post subject: Re: 100A subpanel to my garage
PostPosted: Tue Aug 02, 2011 5:37 pm 
Offline
Global Moderator
User avatar

Joined: Sun Dec 06, 2009 12:26 pm
Posts: 1723
Location: Midlothian Illinois
First Name: Don
Gallery
I did an overhead hook up to my detached garage a while ago. I went to look at the left over wire to see if it was marked with a guage, but just a date. The OD is about 1/4" maybe 5/16, use stranded wire not solid. Everything else, panels breakers etc. the same as you wrote with no issues. I want to say it was #4 but I really do not remember. The longer the run the larger the wire needs to be. Mine was about 50' or so in total.

_________________
Youtube videos I've made
http://www.youtube.com/user/dons69camaro
Some people think I'm out of my mind, but in my defense it's pretty scary in there!


Top
 Profile E-mail  
 
 Post subject: Re: 100A subpanel to my garage
PostPosted: Tue Aug 02, 2011 9:05 pm 
Offline
Global Moderator
User avatar

Joined: Fri Dec 04, 2009 1:13 pm
Posts: 1220
Location: New Lenox IL
First Name: Tom
Gallery
I did a similar deal in my garage buyt I don't recall exactly what the wire gauge was but I think I ran two #2(pretty sure I went heavier than needed becasue that gauge was available for free) and a #10 ground. I know I used 1" conduit to make the run from the inside panel into the garage about 5' away. everything I did I ran past a union electrician buddy first. I will pull the panel front tomorrow for you and let you know

_________________
1980 Z28 Dark Blue w/ Tri Blue Stripes
600hp 383 Carbed SBC
Tremec TKO 600
Ford 9" w/ 3.89's & WaveTrac Posi


Top
 Profile E-mail  
 
 Post subject: Re: 100A subpanel to my garage
PostPosted: Wed Aug 03, 2011 9:11 pm 
Offline
Site Administrator
User avatar

Joined: Sun Nov 29, 2009 8:44 am
Posts: 2622
Location: Yorkville, Illinois
First Name: Jim
Gallery
if you do a search, i've seen charts os amps/wire size vs distance.

Wish I had that kinda power available. I put a 30 amp receptacle on a 20 amp line for the bus, cause I was melting adapters... with the fridge, battery charger, and one of two A/C's running, I'm pulling 21-25 amps, and am only getting 109 volts under than kinda load.

_________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming 'WOW What a Ride!'"

JimM's firstgens.com Camaro Board
Jim's NEW Blog!
http://www.Jimragtop.com
The JimCAM user team p/w camaro
Firstgens on FaceBook


Top
 Profile E-mail  
 
 Post subject: Re: 100A subpanel to my garage
PostPosted: Thu Aug 04, 2011 5:06 am 
Offline
Global Moderator
User avatar

Joined: Sun Dec 06, 2009 12:26 pm
Posts: 1723
Location: Midlothian Illinois
First Name: Don
Gallery
Jim you need a big generator, use it for the bus and when the power goes out with this increasingly wierd weather you'll be covered.

_________________
Youtube videos I've made
http://www.youtube.com/user/dons69camaro
Some people think I'm out of my mind, but in my defense it's pretty scary in there!


Top
 Profile E-mail  
 
 Post subject: Re: 100A subpanel to my garage
PostPosted: Sat Aug 06, 2011 8:32 am 
Offline
User avatar

Joined: Sat Feb 27, 2010 10:22 am
Posts: 44
Location: Palm Coast Fla
First Name: Jerry
Gallery
A minimum size for 100 amps is a #4 copper for the conductors and a # 8 copper for the ground per the NEC.

_________________
68 ss rs convertible clone http://s762.photobucket.com/albums/xx26 ... 26/camaro/


Top
 Profile E-mail  
 
 Post subject: Re: 100A subpanel to my garage
PostPosted: Sun Aug 07, 2011 7:31 am 
Offline
Site Administrator
User avatar

Joined: Sun Nov 29, 2009 8:44 am
Posts: 2622
Location: Yorkville, Illinois
First Name: Jim
Gallery
DHH wrote:
Jim you need a big generator, use it for the bus and when the power goes out with this increasingly wierd weather you'll be covered.


Hmmm, the bus has a big generator... 8000 watts, diesel, variable speed inverter genny. 2 50 amp circuits. Don't think it's actually wired for 220 volts though, 2 125 volt circuits.

Never thought anought bringing it out of the bus though?

_________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming 'WOW What a Ride!'"

JimM's firstgens.com Camaro Board
Jim's NEW Blog!
http://www.Jimragtop.com
The JimCAM user team p/w camaro
Firstgens on FaceBook


Top
 Profile E-mail  
 
 Post subject: Re: 100A subpanel to my garage
PostPosted: Mon Aug 08, 2011 9:07 am 
Offline
User avatar

Joined: Mon Jan 18, 2010 4:35 pm
Posts: 31
Location: Libertyville, IL
First Name: Darrin
Gallery
Thanks - I thought it was either #4 or #3 copper for the hots. That's some pretty big wire to pull though conduit. Good thing it's a short run.

68 vertigo wrote:
A minimum size for 100 amps is a #4 copper for the conductors and a # 8 copper for the ground per the NEC.


Top
 Profile E-mail  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 8 posts ] 

Board index » Community » The Shop

All times are UTC - 6 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 1 guest


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group
Banner

Facebook Connect Login Box

Connect with Facebook



Banner

Facebook Fan Box

myApi - Facebook Activity Box

Facebook Live Box

Facebook Recommendations Box